I'm reviewing a set of drawings for a building remodel. The main switchboard in the building is a 3000 amp board with no room for additional switches. The designer wants to tap directly to the busses in the switchboard and extend conductors sized for a 600 amp load to a fused switch nearby and then to a down stream load.
My thinking is that since the feeder ampacity is less than 1/3 the main board ampacity, that 240.21.B.1 (using 2002 NEC) would apply. Where there is a problem is that in order to maintain proper workspace clearances, the switch will need to be set so that it is more than 10 conductor feet from the point where the conductors are connected to the busses. Is there any relief for this type of a situation written into the code (I could not find any)?
Thanks in advance,
Scott
My thinking is that since the feeder ampacity is less than 1/3 the main board ampacity, that 240.21.B.1 (using 2002 NEC) would apply. Where there is a problem is that in order to maintain proper workspace clearances, the switch will need to be set so that it is more than 10 conductor feet from the point where the conductors are connected to the busses. Is there any relief for this type of a situation written into the code (I could not find any)?
Thanks in advance,