What is the rule for a buss tap on 4000 Amp switchgear for reference voltage on metering equipment (E-Mon D-Mon)? I don't want to use the 10 or 25 foot rule due to the size of wire you would have to use.
 
Do you meet the qualifications to use Part VIII of Article 240? The tap rules in that area are much more liberal for that very reason.

Welcome to the forum. :smile:
 
E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.
 
E-Mon D-Mon

E-Mon D-Mon

E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.
 
230.82 (2005) lists the only items that can be ahead of the service disconnect. It lists load management devices.
 
E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.
Tap off the bus and within 10' of conductor length enter a service entrance rated fused 'safety switch' or an enclosed breaker.
 
E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.

Follow the directions they come with. We just put one in the other day. We used in-line fuses with 1/10A fuses per instructions.
 
230.82 (2005) lists the only items that can be ahead of the service disconnect. It lists load management devices.
But you are allowed to have upto 6 service disconnects, so this section does not come into play if you only have one 'main' and want to add a second one for metering.
 