Tap off the bus and within 10' of conductor length enter a service entrance rated fused 'safety switch' or an enclosed breaker.E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.
E-Mon D-Mon directions show using a breaker for reference voltage, we don't have a breaker that can be used in most applications. I'm looking for a code that would allow me to tap a #12 or #10 to the buss.
But you are allowed to have upto 6 service disconnects, so this section does not come into play if you only have one 'main' and want to add a second one for metering.230.82 (2005) lists the only items that can be ahead of the service disconnect. It lists load management devices.