CelectricB
Member
- Location
- Texas Panhandle
- Occupation
- MEP Designer
In the given one-line, I'm having trouble determining the cable ratings on both the supply and load sides of the 225A fuses that are in 400A rated disconnect enclosures. My current understanding of tap rules would mean that the supply side needs to be rated for the equipment size, or in this case 400A. Load side can be sized to 225A as it is not a tap.
The piece of code confusing me at the moment,
"The ampacity of the tap conductors is as follows:
The piece of code confusing me at the moment,
"The ampacity of the tap conductors is as follows:
- a.
Not less than the combined calculated loads on the circuits supplied by the tap conductors - b.
Not less than the rating of the equipment containing an overcurrent device(s) supplied by the tap conductors or not less than the rating of the overcurrent protective device at the termination of the tap conductors"