I see what your saying, but what we've been saying is that that clause isn't part of the consideration here whatsoever. If a 25ft tap can land on the line terminals of a fused disconnect, then the entire disconnect is an 'overcurrent device' and a 10ft tap that lands on a fused disco meets the second clause after the 'or', regardles of anything the first part says.
I agree that your revision would reduce the confusion.
Edit: actually I don't agree with your revision, due to the following wrinkle. If I can land a 10ft tap on an MLO switchboard of appropriate rating, then I can do so whether it contains one overcurrent device or multiple overcurrent devices. But if there's only one OCPD with the possibility of adding more, I shouldn't be able to use the second clause.
Edit: actually I don't agree with your revision, due to the following wrinkle. If I can land a 10ft tap on an MLO switchboard of appropriate rating, then I can do so whether it contains one overcurrent device or multiple overcurrent devices. But if there's only one OCPD with the possibility of adding more, I shouldn't be able to use the second clause.