RWALKE3117

New member
I INSTALLED A 200A/ 480V 3PH SERVICE WITH 200A FUSED DISCONNECT, RAN FEEDER (3/0 THHN) ABOUT 180' INTO 200A NON FUSED DISCONNECT, INSTALLED MULTI WIRE DEVICE WITH #6 THHN TO 60A FUSED DISCONNECT AND #2 THHN TO 100A FUSED DISCONNECT, BOTH WITHIN 3' TO 6'. I CONSIDER IT TO FALL UNDER THE TAP RULES ARTICLE 240-21 B AND 430-28(1) AND (2). BOTH THE 60A ANS 100A DISCONNECT ARE FOR CONCRETE MIXER MOTORS. THE INSPECTOR TURN IT DOWN FOR OVER FUSING THE TAP CONDUCTORS.
 
Re: TAP RULES

Please turn off the ALL CAPS feature. It makes the post more difficult to read. It is also considered impolite, as though you were SHOUTING at us.
 
Re: TAP RULES

I installed a 200a/ 480v 3ph service with 200a fused disconnect, ran feeder (3/0 thhn) about 180' into 200a non fused disconnect, installed multi wire device with #6 thhn to 60a fused disconnect and #2 thhn to 100a fused disconnect, both within 3' to 6'. I consider it to fall under the tap rules article 240-21 b and 430-28(1) and (2). Both the 60a ans 100a disconnect are for concrete mixer motors. The inspector turn it down for over fusing the tap conductors.

I think this looks so much better.
:)
 