If you go with the tap idea, although I've never done this and most electricians may look at you crosseyed for doing it, code compliant though it may be.
From what I know for branch circuits with taps you can't exceed 50 amps for your circuit wires. But since you load for 15amp devices should be 12 amps or less your circuit shouldn't exceed 48 amps.
Table 210.24, and article 210.19(4) seem to point to a 50 amp circuit with a #6awg run with #12 taps not exceeding 18" long.
May run that by your AHJ first but sounds like a sound installation to me.
On putting panelboards in attics, unless it's a dwelling unit you will be hard pressed to come up with 6-1/2' of headroom 110.26(e). And if you had that you can add a light and switch to your installation 110.26(d). And building codes would also probably require a work platform as well. Rule of thumb IMO...don't put panelboards in attics.