Tap temp power receptacle off of 200 amp main

Status
Not open for further replies.

JP23

Member
Location
California
What is your idea of an easy code compliant way to feed a single 20 amp GFI receptacle from and within 10 ft of
a 200 amp main breaker using the tap rules?
 
Install a fused disconnect or an enclosed circuit breaker rated at 20 amps, and run #12 to the receptacle. That will take all discussions of tap rules out of the picture.
 
use polaris taps in the 200 amp main breaker enclosure, run a conductor rated at 10% of 200 amps to a disconnect with main rated for the tap conductor, install a 20 amp branch breaker and your GFCI. Might be easier to replace the 200 amp main with a panelboard kind of like Charlie said.
 
Replace the 200a Main Breaker with a type that has a Main Breaker with Feed thru lugs that incorporates a small distribution section for your 1p breaker.

Much like an Eaton BR48B200RF.

JAP>
 