That wouldn't be Code compliant.If so, seems like you could tap the range the circuit to provide a 20A OCPD to protect a receptacle for a microwave (IIRC the sections cited in the OP).
That wouldn't be Code compliant.If so, seems like you could tap the range the circuit to provide a 20A OCPD to protect a receptacle for a microwave (IIRC the sections cited in the OP).
What section would that violate?That wouldn't be Code compliant.
210.19. A branch circuit tap has to meet the requirements for branch circuit taps as spelled out in 210.19. What you have described doesn't.What section would that violate?
Constant is not quite a good word.. Think alternating, and its not constant. Also, the most helpful advice is to learn watts and volt load formulas forwards and backwards to really see what happens to current when voltages increase (or decrease, be it in phase degrees or resistance) by any amount. Resistance is second... But not as fun to a wireman (oh, but important). Bam, it alternates and basic load calc! You now know as much as Mr. Holt!I get it now, current is constant in a circuit. So if 40 amps are going through the breaker on one leg, then 40 amps are also going through the other leg. I just had to think about it logically for a second. Did you remember to put cover sheet on the TPS report?
Well, with respect to 210.19, paragraph (A)(3) Exception 1 includes the language "The taps shall not be longer than necessary for servicing the appliance." So that would preclude running the tap conductors any significant distance to a readily accessible location for the OCPD. But if you were able to intercept the existing range wiring at a readily accessible location, then that language would be satisfied. I don't see any other impediments in 210.19(A)(3) Exception 1.210.19. A branch circuit tap has to meet the requirements for branch circuit taps as spelled out in 210.19. What you have described doesn't.
Depends on the context. At any point in time current in a series circuit should be constant across all loads, OCPDs, conductors.Constant is not quite a good word.. Think alternating, and its not constant.
How would you have a "feeder tap" from a 40A "branch circuit."However, 210.19 does not apply to these tap conductors, as they are not branch circuit conductors, since they have downstream OCPD between them and the load. So they would be governed by 240.21(B).
Dude, I like you.This trade is full of oddball ways to remember things.. but some are harmful to continue to elevate our learning and understanding... i wasnt trying to be mean, by far. Or political for once!
Because per the NEC definitions a conductor can obviously be both a branch circuit and a feeder. As the configuration I described demonstrates.How would you have a "feeder tap" from a 40A "branch circuit."
Adding the 20A OCPD makes it a feeder with respect to the receptacle. And 240.21(B) precisely covers the case at hand, where the conductors do have overload protection, but not at their point of supply. Unlike branch circuit taps, where the conductors do not have overload protection.The circuit being tapped is a branch circuit, not a feeder, and is therefore not governed by 240.21(B).
Everyone here had the moment of walking onto a job and suddenly realizing they dont know squat. Everybody.Dude, I like you.
That's certainly not "obvious". In fact, it's obviously incorrect.Because per the NEC definitions a conductor can obviously be both a branch circuit and a feeder. As the configuration I described demonstrates.
The circuit has to be a feeder in order to make a tap to it in accordance with 240.21(B). "Conductors shall be permitted to be tapped...to a feeder..."Adding the 20A OCPD makes it a feeder with respect to the receptacle. And 240.21(B) precisely covers the case at hand, where the conductors do have overload protection, but not at their point of supply. Unlike branch circuit taps, where the conductors do not have overload protection.
Cheers, Wayne
For me, I started binge watching M.Holt videos while I was still in the army 2 years before I got out. Along with many other sources that I won't mention here. But I also made a huge investment purchasing his training library and studying that. Day 1 of when I started in the trade, I knew a lot of things that others i worked with didn't know. Plus I had a code book which very few people had.Everyone here had the moment of walking onto a job and suddenly realizing they dont know squat
I agree, obvious was a poor choice of words. But there's nothing in the definitions of branch circuit and feeder that makes them mutually exclusive.That's certainly not "obvious". In fact, it's obviously incorrect.
And adding that 20A OCPD makes it a feeder. I agree that if there were no downstream OCPD, then it couldn't be a feeder tap, and would be a branch circuit tap.The circuit has to be a feeder in order to make a tap to it in accordance with 240.21(B). "Conductors shall be permitted to be tapped...to a feeder..."
Of course there is. When I have my 40A branch circuit that I propose to tap....The 40A c/b is the final overcurrent device protecting the circuit.I agree, obvious was a poor choice of words. But there's nothing in the definitions of branch circuit and feeder that makes them mutually exclusive.
Until you add another OCPD in the manner I suggested, and then it is no longer the final overcurrent device with respect to at least one of the outlets. While remaining final with respect to another of the outlets. "Final" is relative to a given endpoint.When I have my 40A branch circuit that I propose to tap....The 40A c/b is the final overcurrent device protecting the circuit.
There may be no overlap if there is an NEC section that prohibits the arrangement I described in my last post. If there is no such prohibition, then that arrangement demonstrates that the definitions may (rarely) overlap. The definitions are outlet-specific, and the status of a conductor may vary depending on the outlet referenced.A feeder is the circuit conductors between the source and the final branch-circuit overcurrent device. A branch circuit is the circuit conductors between the final branch-circuit over current device and the outlet(s). There is no overlap.