I've got a 350kW generator with a 600A main feeding into a wireway off of which I want to tap for my Life Safety, Critical branch, Equipment branch, etc (obviously for a hospital).
My concern is that I'll have two conductors per phase comming into that wireway and will have to tap off via each phase to each branches breaker.
I normally stear clear of tapping off a wireway like this when I've got multiple conductors per phase but with the 2008 codes isolation requirements for emergency distribution systems, I prefer to go this route to having a huge switchboard with each section having a single, relatively small circuit breaker.
I'm wondering what kind of trouble I might get into here when the electrician goes to actually implement this. The first thing that occurs to me is that the minimum size for parallel conductos is a 1/0. So for my feed to my 150A LS ATS, I'll need to come off with two 1/0's.
Do you agree?
Any comments would be appreciated.
Thanks,
Mike
My concern is that I'll have two conductors per phase comming into that wireway and will have to tap off via each phase to each branches breaker.
I normally stear clear of tapping off a wireway like this when I've got multiple conductors per phase but with the 2008 codes isolation requirements for emergency distribution systems, I prefer to go this route to having a huge switchboard with each section having a single, relatively small circuit breaker.
I'm wondering what kind of trouble I might get into here when the electrician goes to actually implement this. The first thing that occurs to me is that the minimum size for parallel conductos is a 1/0. So for my feed to my 150A LS ATS, I'll need to come off with two 1/0's.
Do you agree?
Any comments would be appreciated.
Thanks,
Mike