tapping off of an existing circuit

Status
Not open for further replies.

sybrandy

Member
Is there any way I can tap off of an existing circuit, protected by a 20 amp breaker, to feed two 15amp receptacles with #14 awg??
 
sybrandy said:
Is there any way I can tap off of an existing circuit, protected by a 20 amp breaker, to feed two 15amp receptacles with #14 awg??

You could also make the tap as long as you used #12 awg, as long as it wasn't a dedicated circuit.
 
why ?

why ?

infinity said:
Why would you want to do this in the first place?

The standard answer I get in the field is "I already had some #14" :grin:
 
sybrandy said:
. . 20 amp breaker . . . #14 awg
There's the problem: the breaker must be sized to the wire. The 15a receptacles are not an issue.

Where is Sy anyway? :confused:
 