How hard is it to "tap" (not a tap lol) and get 8 sets of 3#500s from a single switchboard?I think we should not use the word tap since these are just normal feeder conductors.
Nice idea but then they would be taps and they are not close enough to meet the tap rules.
Even if there is no room for a new switchboard near the existing one perhaps there is room for some fused disconnects. Then you could potentially tap to them and then feed to the chillers.
Here's a pic of 1 for reference: