I don't read it that way.Your opinion baffles me. :blink:
You only need to look to the section right before the one you quoted (i.e. 705.12(D)(1)) to see that a dedicated OCPD is required for the inverter(s) no matter which way they are connected.
I thought that issue was already settled.It's weird that you don't want to discuss the provision that applies to the OP's question.
Again I don't read the sections that way. We will have to agree to disagree on this one.And you only need to look at the section right after the one you quoted (705.12(D)(2)(2) to see that 240.21(B) is still in force. The rules don't modify the rules if they don't actually modify them.