Section 240.21 (1)b can this rule be applied to the conductors between the load side of the meter and the first overcurrent device?
I would say no. Section 240.21(B) is for feeder taps. Any conductors ahead of the service disconnect will not be a feeder.Section 240.21 (1)b can this rule be applied to the conductors between the load side of the meter and the first overcurrent device?
No, nothing in Article 240 applies to service conductors and the conductors between the meter and the first OCPD are service conductors.Section 240.21 (1)b can this rule be applied to the conductors between the load side of the meter and the first overcurrent device?
Sorry, where does Article 240 say that?No, nothing in Article 240 applies to service conductors and the conductors between the meter and the first OCPD are service conductors.
Ok, I will revise that...nothing in240 applies to the conductors in this thread as they are not tap conductors as defined in Article 100.Sorry, where does Article 240 say that?