I think if you backtrack to 210.19(A)(3) Exc. 1, or 210.19(A)(4) Exc. 1a and 1b, you'll find an answer.
 
Last edited:
bobrenwick said:
In Table 210-24 what is the meaning of the word Taps?
Tap Conductors. As used in this article (Article 240, not Article 210), a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
The definition is not referred to in 210-24, which is just a summery, but 240(E) refers back to Article 210. :smile:
 
electricalperson said:
i dont know if im explaining this right, but basically a tap is when you attach a wire to another wire using either a split bolt or a connector.

Basically, a tap is a connection of a smaller conductor to a larger conductor without a properly sized overcurrent protective device.
 
So on a residential 20 amp lighting circuit one could use a 14 awg for the switchleg to an individual fixture? I always thought you needed 12 awg all the way through.
 
bobrenwick said:
So on a residential 20 amp lighting circuit one could use a 14 awg for the switchleg to an individual fixture? I always thought you needed 12 awg all the way through.

Who said you can do that? When used as a "general" branch circuit, #14 is limited to a 15A max OCPD. There are no rules in article 210, 240, or 310 that modify this requirement.
 
jim dungar said:
Who said you can do that? When used as a "general" branch circuit, #14 is limited to a 15A max OCPD. There are no rules in article 210, 240, or 310 that modify this requirement.

I was looking at 210.19 (A) (4) ex 1a, but I guess that applies to the fixture wires.
 