Mike01My recent dilemma consist of a main switchboard with a 600AF/600AT LSIG C.B. (480V) to a MLO distribution panel (600A-480V-3PH-3W) the panel contains multiple 250AF/125AT LSIG C.B. that feed into a 75Kva xfmr said:
I have a selectivity chart from Square D, that was created by actual factory tests, that coordinates even if the curves show an overlap. For selectivity, with up to 65kSCA @ 480V, their circuit would be:
a PJ 1200AF/100AT breaker to a 75kVA transformer, the secondary main breaker would need to be an LA-MC 400AF/250AT and the branches breaker could be the normal QO/QOB up to 100A.
Have you thought of using a transformer smaller than 75kVA?
Can you turn off the I function of your 600A main?