TCC Square D 3 Pole ML (225A)
EduAc
Calgary
Electrical Engineer
Hello Guys.
I want to know if someone has the TCC curves from old (Obsolete) Square D ML 3 Pole Circuit breakers (200A,225A,100A,). I am trying to model this ones in ETAP but couldn't find the catalog, manual or TCC yet. Here an image of those guys
Thanks
Hello Guys.
Thanks
ML is a type number of panels that was not always descriptive of the breaker that was installed in it. The breakers had part numbers (on their sides) like 999xxx or 997xxx.
Some of the small breakers were called ML, ML-1, or ML-2, the earlier 225A breakers were ML-3. In later part of the 50s, the 225A were type LA (actually they were brand labeled type JKL).
The breaker in your picture is number 997xxxx which is a type ML-3.
Thanks Jim,
I'm trying to find the trip curve for a 3-Pole 9973 225A ML-3. and 3-Pole 9973 200A.
I am out of town for several weeks, so I cannot look.
The ML-3 curve ends at 10kA, so that is its rating.
The horizontal axis is % of breaker rating though, so it is 100 time whatever the breaker rating is. Thanks!
You are right, it does extend past the 100X rating.
This breaker was produced before the current way SCCR and AIC are tested and reported, which occurred in the 1980s.