Telephone and cable bonding for new construction

Status
Not open for further replies.

powerplay

Senior Member
I was told to connect the demarcation box for the tel and cable with separate insulated #6 copper wire back to the panel. Is it necessary, or can I run the #6 through one box then carry through to the other?
 
There can be no complaint in using a single #6 wire to bond multiple other systems as that is all 250.94(3) requires to be provided as the connection to the service.
 
You might need to look at the requirements in Article 800.

1100796698_2.jpg
 