Can someone tell me if work space for telephone equipment is regulated by a code or standard. For example 3' clearance in front of equipment.
 

aksun45

Member
Location
ak
Thanks,
I wasn't sure if low voltage telephone equipment, specifically punch down blocks were covered in 110.26 or another code.

Thanks again
 

jumper

Senior Member
If it did not apply to low voltage this exception would not exist:

(b) Low Voltage. By special permission, smaller working
spaces shall be permitted where all exposed live parts
operate at not greater than 30 volts rms, 42 volts peak, or
60 volts dc.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The telephone equipment would be covered by a Chapter 8 article. The rules in Chapters 1-7 do not apply to Chapter 8 articles.
90.3 ...Chapter 8 covers communications systems and is not subject to the requirements of Chapters 1 through 7 except where the requirements are specifically referenced in Chapter 8.
 

aksun45

Member
Location
ak
Thanks Don, it appears telecom work spaces is deferred to "ansi tia-570-b work spaces" . But I am still having a hard time coming up with definitive numbers and distances.
 