Temp Riser

FYI: The tap rule comes into play when the conductor can carry the load but is protected by a breaker with a higher than the ampacity of the conductor. Because you have 100 amp breakers in your panel you need a 100 amp conductor supplying the panel but your feeder is 400 amps,.
The tap rules (240.21) allow you to use that 100 amp conductor being protected by the 400 amp breaker under specific conditions such as length of conductor, termination requirements, etc.
 
So if each panel calc load was 50A @ 120/208v and I had 8 panels as shown I would need 400A.

I could run (2) sets of 4/0. One set feeding 4 panels and the other set the other 4. I can't terminate the 4/0 directly in the panel can I?
 
So if each panel calc load was 50A @ 120/208v and I had 8 panels as shown I would need 400A.

I could run (2) sets of 4/0. One set feeding 4 panels and the other set the other 4. I can't terminate the 4/0 directly in the panel can I?
Unlikely that a 100 amp breaker would accept a #4/0. Using two #4/0 risers would also work as long as you have two 200 amp breakers at the origin of the feeder.
 
Maybe I'll just figure 50-60A circuits to each 100A temp panel individually and let field figure it out if we get the job.
Maybe even be able to feed them with romex depending on size I need after voltage drop for further ones but I may get into trouble figuring 50-60A circuits because if the wind up using 100A I'm screwed.
 