I've read some of the other threads on this topic, and I understand that while equipment may be provided with 90C lugs, it is likely tested and listed at 75C. I'm trying to find out if this is the case for some 1,500VDC equipment (i.e. inverter, combiner box, disconnect) for a design in order to size the cable. The datasheets for the equipment in question all say the lugs are rated at 90C. I reached out to the manufacturers and asked if the equipment is listed to 75C or 90C, and they all replied 90C. I'm a bit skeptical since all the threads on this site say that barely any equipment is listed at 90C.
Should I ask the equipment manufacturers for the UL listing to get a definitive answer on the temperature rating? Has anybody else gone down this path for 1,500VDC equipment?