I think this is one of the most confusing parts of the NEC. I quess this question has two parts.
#1 does anyone know of any good software that will calcuate a combimed temperature derating with more than three wires in a conduit?
#2 I have two small moters, one a 1/2 hp Maint Hoist, that will almost never be used, and a 30 hp lubercation pump motor. 480V, ambient temperature of around 100 Deg F in an Arizonia copper mine. THHN wire. I want to put the 6 wires in the same conduit. 150' total distance from the MCC so voltage drop is not a factor.
No motor derating on the 1/5 hp motor because it will be almost never used.
So here goes, do I use 75 or 90 degree table to derate the wire and then use the min wire size based on 75 degree lugs? Then deratte for temp and then for 6 conductors in the same conduit?
So confused
Ken
#1 does anyone know of any good software that will calcuate a combimed temperature derating with more than three wires in a conduit?
#2 I have two small moters, one a 1/2 hp Maint Hoist, that will almost never be used, and a 30 hp lubercation pump motor. 480V, ambient temperature of around 100 Deg F in an Arizonia copper mine. THHN wire. I want to put the 6 wires in the same conduit. 150' total distance from the MCC so voltage drop is not a factor.