The only place I know of where we use the motor "T" rating is for classified areas. I would not want to calculate my own "T" rating. I would want that information from the manufacturer and on the nameplate.
Agreed, but NEC 501.125(B) allows squirrel cage motors
without labeling for Class I, Division 2 locations provided there are no switching, sparking and arcing mechanisms AND surface temperatures do not exceed 80% of AIT
.
If I have a general purpose 460V motor, say a Baldor- Reliance VEM3558, I'd take 40 deg C ambient and maximum 65 deg C rise on the windings, (105 deg C) and compare this to the Area Classification drawings/AIT's to determine a relative 'T-rating'.
Where am I wrong?