Say you have panels A and B. A is getting it's permanent feed redone. Put a 100 amp breaker in each panel (or however you are going to make some temp connections). Run a feed between those two breakers. Check phasing, energize. Remove and reinstall feeder to panel A, turn off breakers and remove temp feed.
Bonus for having some fun with your apprentice or the new guy (not that I would be having them do hot work). Hide a delta -wye transformer with a 1-1 voltage ratio somewhere to create a 30 degree phase shift, ask apprentice why it's taking him so long to phase out that temp feed