T Tim Kennedy New member May 10, 2005 #1 Do all branch circuits have to be GFCI protected on a construction site?Or just those that serve hand held tools?
Do all branch circuits have to be GFCI protected on a construction site?Or just those that serve hand held tools?
B bphgravity Senior Member Location Florida May 10, 2005 #2 Re: Temporary construction service The branch circuits are not required to be protected, only the receptacles. All 125-volt, 15,20,and 30-ampere receptacles. Receptacles other than these must have GFCI protection or an assured EGC program. See section 590.6 (2005 NEC)
Re: Temporary construction service The branch circuits are not required to be protected, only the receptacles. All 125-volt, 15,20,and 30-ampere receptacles. Receptacles other than these must have GFCI protection or an assured EGC program. See section 590.6 (2005 NEC)