I guess these things are just unsafe. ...
What specifically do you think is unsafe?
...
I guess these things are just unsafe. ...
this would appear to be a clear code violation. the N-G bond is only allowed to be at one point. I think to be code compliant you would need to seperate the N-G at the generator end.Our generators are bonded and so are the buildings main disconnects, so if we have a neutral we don't install a EGC for obvious reasons. These installations are not code compliant.
I think he is making a joke.What specifically do you think is unsafe?
Or switch the neutral.this would appear to be a clear code violation. the N-G bond is only allowed to be at one point. I think to be code compliant you would need to seperate the N-G at the generator end.
the code also requires an EGC be run with the circuit conductors so if you are not running one, that is also a code violation.
There's only one N-G bond. The generator frame is not G if there's no grounding electrode.this would appear to be a clear code violation. the N-G bond is only allowed to be at one point. I think to be code compliant you would need to seperate the N-G at the generator end.
the code also requires an EGC be run with the circuit conductors so if you are not running one, that is also a code violation.
The code allows for multiple grounding electrodes to be connected in multiple places. You just cannot have a N-G bond in more than one place.There's only one N-G bond. The generator frame is not G if there's no grounding electrode.
I don't see what section requires an EGC. 230.35 (B) requires an SSBJ but that's for 'Permanently Installed Generators' which this is not.
The setup appears to comply with 250.34(2).
Two, NG bond in panel and at genset. Absence of a GE, if frame is on the earth, only creates potentially a high impendence ground, where the Neutral is bonded to frame.There's only one N-G bond. The generator frame is not G if there's no grounding electrode.
Check out requirements in article 445I don't see what section requires an EGC. 230.35 (B) requires an SSBJ but that's for 'Permanently Installed Generators' which this is not.
The setup appears to comply with 250.34(2).
Check out requirements in article 445
Can't read your link but it's irrelevant, workbook illustrations are not binding. The third option being talked about is no EGC, bonding at both ends. This is how services are done and it used to be allowed for outbuildings, too. What is the danger?2020 NFPA 70 Workbook illustration related to 445.11 enhanced content. in Link
NFPA LiNK®
The leading information and knowledge resource on fire, electrical and related hazards.link.nfpa.org
At genset, without a NG bond, EGC bonds to main panel and no GE at Genset,
A genset With NG bond, Neutral required to be switched, and still has EGC and but has a GE at Genset.