Temporary O.H. weatherhead location

Status
Not open for further replies.
Art. 590 is for temp. installations however , 590.4 states services shall be installed in conformance with art. 230. I don't believe you will find relief on a temp. service. Heights are dictated by the power company in our area. The tell us what size pole etc.
 
230.54 (C)
Exception: Where it is impracticable to locate the service head or gooseneck above the point of attachment, the service head or gooseneck location shall be permitted not farther than 600 mm (24 in.) from the point of attachment.
 
both are correct and also make sure you check with the POCO for the lastest info sometime they will change at the last minuite if the situation don't meet either code

most of the POCO regulation book will give you pretty good detail some case they will including a photo what it look like as well.

Merci,Marc
 