I believe the poster of the pic or should I say the one that tried to post it stated it was the UK. Pretty nice setup really. MUst have cost a pretty penny er pound or pince or whatever ;)
 
Rentalguy said:
Does an outdoor temporary distribution panel require a main breaker?
If it has over six handles as per 230.71 A (which it probably wouldn't) and it was service equipment Yes, Main required.
If it was a feeder as George pointed out and it had proper overcurrent protection on the feeder feeding the panel with 24 o.c.d. in it then it would not be required as in 590.4 (B). I think.:smile:
 