I am looking to have some distribution panles built for temporary electric use outside. The Panels are a Nema 3R and have flush mounted Cam-lok connections as an input. These are rated at 405 amps. The output will be either L21-30 or L21-20 twist-locks put on a 30 or 20 amp 3-pole breaker. There will be 6 of the twist lock outputs. My questions is a 400 amp disconnect ok to use as the means of disconnect. I will be coming of a 225 kw generator (800 amp main) with a 10-15ft set of 4/0 tails. Then feeding the panel with 4/0 Type W. My biggest question is does the distro panel need a main disconnect? The distro panel will have the 30 amp breakers protecting the number 10 and the 400 amp protecting the flush mounts. Can I go from the flush mounts to the line side of a 30 amp breakerwith # 10? I hope this makes sense. Thanks for your time. If you could let me know where in the code you are basing an answers on.
Dave