When calculating conductor size for a temporary "overhead" service drop, do you need to derate the conductors if the they are installed in a pipe? (3 phase 4 wire 480 volt service)
For instance I need to supply a 480 volt 400 amp temp service. I had considered using two risers (2 1/2") containing 4 - 4/0 copper THHN with a #2 copper ground.
Is the 4/0 too small because of derating? (4 current carring conductors in a pipe 80%)
Or should I go to 4 - 250 Kcmil copper?