Are multiconductor cables required for temporary feeders, per 590.4? Or could cables with single conductors also qualify as a "cable assembly"?
590.4(B) - ....Conductors shall be permitted within cable assemblies or withing multiconductor cords or cables of a type identified in table 400.4 for hard usage or extra-hard usage.
For example, I can get type W portable power cable with up to 5 conductors, which would be allowed per the above quote. But type W portable power cable is also available in single conductors.
Am I reading the code right? The multiconductor cables are allowed, but not the single cables, even though they have the same listing as type W?