terminal and conductor heat

Status
Not open for further replies.

megloff11x

Senior Member
My understanding of the drill if you have differently termperature rated terminals and conductors is as follows:

If the terminal is rated at a lower temperature than the conductors, your minimu conductor size is based on ampacity at the lower rating. For example, if I have 100A into a 60C rated terminal, I must use a minimum of 1AWG wire, which is rated 110A at 30C by table 310.16.

If I use higher temperature rated wire, it must still be minimum 1AWG to draw heat off the terminal.

Now, if things get warmer, let's say 40C environment, if I was using 60C rated conductors, I would derate by 0.82 and need a conductor with an effective ampacity of 122A (100A/0.82). Thus I'd need 1/0 which goes to 125A.

However, if I was using THHN rated at 75C, my conductor derate is 0.88 for effectively 113A. This 75C column gives 2AWG wire at 115A, but my terminals still need 1AWG because they're 60C rated.

If I had these conductors bundled in a conduit run, I would need further derating there for them. In any case, I have to use the bigger of what the 60C terminal needs at ambient 30C regardless of temperature, or conductor based on temperature and bundle derating. Using a higher temperature rated conductor lets you stay thin at higher temps and bigger bundles, as long as it's thick enough for the terminal at 30C.

1. Does the terminal minimum conductor size depend on actual temperature ever, or do we just calculate that size at 30C (nominal table values)? At some point I would think the warmer terminals might want a fatter still conductor to help remove heat, but if I read the current method correctly, we don't do this. Do we ever consider bundling on heat removal as well?

2. Is this the correct way to do this? I prefer to divide the calculated load amperes by the deratings and look up at nominal 30C table values rather than multiply the whole 30C table 310.16 by the deratings and try and find it that way. It seems to go quicker my way.

Matt
 
I dropped off in following the numbers after 30? C. Sorry

I'll try to answer with this:

100 Amps or less
Wire size #14 - #1
60?C ampacity

Over 100 Amps
Wire Size #1/0 and larger
75?C ampacity

110.14(C) ... the temperature rating assoiciated with the ampacity of the conductor shall be selected so as not to exceed thd lowest temperature rating of any connected termination, conductor, or device. Conductors with tempertures rating higher than specified for termination shall be permitted to be used for ampicity adjustment, correction, or both.

(Our)Electrical equipment terminations are rated at 60?C, 75?c or 65/75.

Overall what this temperture represents is it's tested and appliable service limit. Yes one has to derate if there's some constant ambiant tempeture situation, is that where the 30?'s is coming from. (maybe I missed that)

For example theres all kinds of mis-applications that could arise from heavly loaded 60? wire on a 75? breaker,see above
Even using 90? wire on a 75? breaker, which is often incorrect if also fully loaded.

WIT to protect the wire then breaker that service... thats the way I learned it.
 
Last edited: