maxbillington
Elec Engineer, Adjunct Faculty
- Location
- Colorado
- Occupation
- Prof Engineer
I have a school installation in which the contractor has terminated plenum rated IT system cables to plastic connectors within the plenum. The connectors mount on a video projector mounting plate that faces down into the room. The contractor did not use a back box to enclose the terminations.
I have pointed out the following code paragraphs:
The NEC 300.22 Wiring in Ducts, Plenums, and Other Air-Handling Spaces requires all cables installed in a plenum space to be in raceways, or plenum rated cable.
Article 300.15 Boxes, Conduit Bodies, or Fittings ? Where Required. "... a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point..."
The contractor's response is that Article 300 does not apply to communications cables.
So here is my question:
Are IT cable terminations in a plenum required to be within a box?
I have pointed out the following code paragraphs:
The NEC 300.22 Wiring in Ducts, Plenums, and Other Air-Handling Spaces requires all cables installed in a plenum space to be in raceways, or plenum rated cable.
Article 300.15 Boxes, Conduit Bodies, or Fittings ? Where Required. "... a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point..."
The contractor's response is that Article 300 does not apply to communications cables.
So here is my question:
Are IT cable terminations in a plenum required to be within a box?