This is the reply of a question submitted for clarification ;
Q: I want to secure #12 AWG THHN stranded conductors to the screw terminal of wiring devices, duplex receptacles and/or toggle switches, even though the stranded conductor spreads and does not make full contact with the screw terminal and remains undamaged throughout the maneuver. Can I just wrap the stranded conductor around the screw terminal and tighten using a torque screwdriver or must I use a T & B Sta-Kon crimp terminal to prevent the strands from spreading? There is another method that comes to mind, strip a small portion of insulation and allow it to cover the tip of the strands, thereby minimizing the amount of spread at the conductor end. If I must use a crimp terminal or some other method, please explain why since there is no mention of this in Section 110.4 or anywhere else in the Code.
I understand some contractors have received a violation on this matter using section 110.14 of the Code.
A. UL Listed receptacles are evaluated for use with solid and stranded conductors. Also, 2012 UL White Book permits terminals of a receptacle are permitted for use with certified field-installed crimped-on wire connectors or an assembly, if so identified by the manufacturer. (Refer to UL product category RTRT).
General use switches are Listed for use with only solid conductors unless otherwise indicated in their installation instructions. 2012 UL White Book doesn’t include permitting language to use certified crimped-on wire connectors or an assembly. (Refer to UL product category WMUZ).