termination of paralleled conductors
sshane
New member
A 400 amp main feeds 2 panels, the feed comes underground and into 1 panel that feeds to the other panel adjacent to each other. Parallel feeds split in two 2" pipes, could I feed 1/2 of the paralleled feed into 1 panel and half in the other and jumper between panels with paralleled feeders
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
I don't see how you could could the lengths equal. Can you install a trough under the panels tap from there? It is an interesting question and have never seen it done that way. I just don't see how it could work.
infinity
New Jersey
Journeyman Electrician
uc
This would make the conductors tap conductors and would therefore need to follow the tap rules in Article 240.
Welcome to the Forum. :D
charlie b
Seattle, WA
. . . could I feed 1/2 of the paralleled feed into 1 panel and half in the other and jumper between panels with paralleled feeders
If you do that, the conductors will no longer be in parallel. But why should they be anyway? Why do they need to be in parallel? If you supply two panels from the same source, each will normally get its own feeder.
infinity
New Jersey
I think that the issue is he has a 400 amp OCPD to feed 2-200 amp panels. That kind of limits his options.
petersonra
Northern illinois
engineer
If he jumpers them at the end as he said in his OP they are now paralleled.
310.4 Conductors in Parallel. Aluminum, copper-clad
aluminum, or copper conductors of size 1/0 AWG and
larger, comprising each phase, polarity, neutral, or
grounded circuit conductor, shall be permitted to be connected
in parallel (electrically joined at both ends).
I would say he has electrically joined them at both ends.
petersonra
Northern illinois
engineer
As far as I can tell, the code does not prohibit "ring" circuits as long as they meet all the requirements of paralleled conductors. The critical one being they have to be 1/0 or larger.
jim dungar
Wisconsin
Engineer
But I think the real issue is the 200 amp panels as Rob mentioned,
Did I miss where the OP said they actually were 200A panels?
This is not the first time I have been asked this question. Both conductors into Panel 1 and then looped over to Panel 2 requires a second set of lugs. One set into Panel 1, the other set into panel 2, and a jumper between them can physically be done with one set of lugs.
infinity
New Jersey
You're right, he didn't say 2-200 amp panels I made that assumption. :eek:hmy: Maybe he will check back in and clarify.
iwire
Massachusetts
why would it matter. as long as the feeder wires are protected properly does it really matter what size the PBs are?
If the panelboards are MLO 200s and protected by a 400 amp over current device that would be a violation. But as Charlie said we don't really know anything.
infinity
New Jersey
Like Bob said a 200 amp MLO on a 400 amp feeder would be a problem.
petersonra
Northern illinois
engineer
Good point. I would not likely ever spec out a MLO panel, so that had not occurred to me. In any case, the OP only asked about the way he paralleled the conductors. There are all kind of other things he might have done wrong, like not derating since he has at least (6) CCC in the 4" conduit.