Pretty sure, if the circuit consists of only such devices. If the circuit contains other devices such as starters, contactors etc., your cable can not be used again at its full load capacity.Just for you......
Table 2 clause 7.2.2.1 of IEC 60947-1 details the permissible temperature rise based on the type of metal used in the construction of the terminals.
For example, where the terminals are made of silver plated or nickel plated copper or brass, the maximum rise above ambient is 70 K, resulting in a maximum termination temperature of 110C.
K is for Kelvin.
Will you now give me your kind consent to employ XPLE at it's full rating for this particular device?
Pretty please?