Care to explain why?
Well.
I think you did not study the link in post # 28 or the observation in post # 30.
The link in post # 28 states that for 65C temperature rise terminals of IEC starters and contactors, 75C rated conductors are required.
Again take a look at post#30.
Can you show any evidence ( such as mentioned in any application manual) that 90C rated conductor may be used at its full rating for the IEC contactors you mentioned in post # 23.