H holiday Member Feb 24, 2005 #1 unless listed & identified otherwise, terminations & conductors of circuits rated 100 amps or more shall be rated ta what? degree.
unless listed & identified otherwise, terminations & conductors of circuits rated 100 amps or more shall be rated ta what? degree.
bob Senior Member Location Alabama Feb 24, 2005 #2 Re: terminations& conductors of circuits See 110.14(C)1
K kiloamp7 Senior Member Feb 24, 2005 #3 Re: terminations& conductors of circuits This sounds like a test question. If it is a real question, look closely, most modern stuff is rated for 75 degree centigrade terminations.
Re: terminations& conductors of circuits This sounds like a test question. If it is a real question, look closely, most modern stuff is rated for 75 degree centigrade terminations.
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Feb 24, 2005 #4 Re: terminations& conductors of circuits If this was an exam question I think it has been misstated a bit. Check 110.14(C)(1)(b)
Re: terminations& conductors of circuits If this was an exam question I think it has been misstated a bit. Check 110.14(C)(1)(b)