unless listed & identified otherwise, terminations & conductors of circuits rated 100 amps or more shall be rated ta what? degree.
 
Re: terminations& conductors of circuits

This sounds like a test question.

If it is a real question, look closely, most modern stuff is rated for 75 degree centigrade terminations.
 
Re: terminations& conductors of circuits

If this was an exam question I think it has been misstated a bit. Check 110.14(C)(1)(b)
 