I recently installed a Tesla charger on an exterior wall for a customer. I used #6 Copper Thwn -2 90* rating in 1" pvc underground transitioning to emt risers. The run from the sub panel is 35'. The sub-panel is 125 amp. This Tesla charger requires a 240v 60 amp breaker. I wired it as instructed with 2 energized lines, a ground, and properly torqued lugs using the recommended manufacturer breaker for the panel. Within 3 days it completely fried the breakers in the panel. The breakers were smoking, but the 60 amp Tesla breaker had not tripped and was completely melted. The heat from that breaker melted several others. That breaker was brand new. I purchased it the day I installed it. I have read several posts online stating not to install a Tesla charger on anything less than a 150a rated panel, however, Tesla denies this is a problem. I spoke to another electrician here in town and he stated he has had 2 breakers burn up after installing Tesla chargers. I'm in Lake Havasu City, Arizona, so it is not uncommon for temperatures here to be well into 100-125 degrees. I believe the day this burned up it was about 114. I recently swapped out the pane for a 200a using a 125 main. I have been doing some testing. The amp draw is anywhere from 42-28 amps. Breaker temperature is running 127-136 degrees. ANY SUGGESTIONS OR ADVICE?