bclumen
Member
- Location
- Elkridge, MD
We had a Tesla wall charger install fail inspection. It has adjustable output 12A-80A. We fed with a 50A ckt. and since its mechanicaly adjustable and could be adjusted to draw 100a, the inspector is requiring a 100a cable be installed to it. In your opinion, does 625.40 apply here? Is the max rating the setpoint we set it to or the maximum it could be set to? I'm a bit stumped as only one jurisdiction has required this and we've done similar installs in other counties.