Tesla Charger

frofro19

Senior Member
Location
VA.
Occupation
Master Electrician
Just to be sure, if I use 6-6-8 CU SEU, that can be on a 60 amp breaker for a Tesla charger set at 48 amps and SEU can be used in the 75 ° column and that's good for 65 amps, correct? I'm assuming the difference between SEU, that can be used in the 75° column and Romex has to be used in the 60° column is the insulation?
 