I should have known that. Thank you!
Too small to satisfy 210.19(A)(1), but as far as I can see, not too small to be safely used in this application. 210.19(A)(1) should just be deleted, as 210.20(A) plus 240.4 is sufficient.It's really no mystery. 48*125%= 60 amps. #6 AWG NM cable is only good for 55 amps so it's too small.
My garage is currently unfinished. I asked one of the electricians about installing THWN-2 in conduit and he said that it would be "too much work" to run EMT inside the wall through holes in the garage studs. It would be about a 20 foot run up from the electrical box, around the side door and down the other side (so two or three 90 degree bends).It's really no mystery. 48*125%= 60 amps. #6 AWG NM cable is only good for 55 amps so it's too small. Use MC cable or conduit and wire and #6 is good for 65 amps.
It's good to know that there's no safety issue for the sake of all the other customers who now have #6 romex installations.Too small to satisfy 210.19(A)(1), but as far as I can see, not too small to be safely used in this application. 210.19(A)(1) should just be deleted, as 210.20(A) plus 240.4 is sufficient.
Cheers, Wayne
FMC is an option thru the studs too, and then pulling in the THHN.My garage is currently unfinished. I asked one of the electricians about installing THWN-2 in conduit and he said that it would be "too much work" to run EMT inside the wall through holes in the garage studs. It would be about a 20 foot run up from the electrical box, around the side door and down the other side (so two or three 90 degree bends).
Another electrician suggested using smurf-tube. Is that code compliant for the purpose of housing THWN cable?
I don't see "MC" mentioned in Table 310.16 here so I'm not sure how one would determine if the rating is sufficient or not. But it looks more flexible and easier to install than EMT with THWN inside.
Do you have any specific MC cable you know for sure would be good for running a Tesla charger at the full capacity?
Preferably steel clad rather than aluminum since it is less likely to be punctured by someone carelessly shooting a nail gun while redoing the siding 10 years from now.
If you want to use #6 AWG conductors you need a wiring method that can utilize their 75° C ampacity. MC cable, SE cable, or conduit (EMT, FMC, ENT, etc.) and wire can use the 75° C ampacity. NM cable cannot due to 334.80 which limits it to 60° C.My garage is currently unfinished. I asked one of the electricians about installing THWN-2 in conduit and he said that it would be "too much work" to run EMT inside the wall through holes in the garage studs. It would be about a 20 foot run up from the electrical box, around the side door and down the other side (so two or three 90 degree bends).
Another electrician suggested using smurf-tube. Is that code compliant for the purpose of housing THWN cable?
I don't see "MC" mentioned in Table 310.16 here so I'm not sure how one would determine if the rating is sufficient or not. But it looks more flexible and easier to install than EMT with THWN inside.
Do you have any specific MC cable you know for sure would be good for running a Tesla charger at the full capacity?
Preferably steel clad rather than aluminum since it is less likely to be punctured by someone carelessly shooting a nail gun while redoing the siding 10 years from now.
With that in mind, you probably should lean towards installing conduit and even oversizing the conduit so larger conductors can be installed in the future.if that means that the wire also has some additional amperage headroom, that's not a bad thing since it's not unlikely that EV chargers with higher amps will become even more commonplace in the future.
Would ENT (smurf tube) be sufficient as a conduit or would a EMT be required. I am thinking that a continuous load of 48A running though wires encased in closed cell foam for 6 hours will likely cause the temperature inside the conduit to exceed 50C. Isn't 50C is the limit for ENT?With that in mind, you probably should lean towards installing conduit and even oversizing the conduit so larger conductors can be installed in the future.
The 50° C limit is for ambient temperature outside of the conduit. I don't see an issue with using #6 AWG conductors. If it concerns you then you can use larger conductors.Would ENT (smurf tube) be sufficient as a conduit or would a EMT be required. I am thinking that a continuous load of 48A running though wires encased in closed cell foam for 6 hours will likely cause the temperature inside the conduit to exceed 50C. Isn't 50C is the limit for ENT?
Thus my suggestion for FMC or Flex. Not sure of temperature rating of ENT, but do know there are a couple of differently rated ENT. There is the orange (innerducting) that is used almost strictly for LV. Then there is the blue that I've seen used for both 600V and LV.Would ENT (smurf tube) be sufficient as a conduit or would a EMT be required. I am thinking that a continuous load of 48A running though wires encased in closed cell foam for 6 hours will likely cause the temperature inside the conduit to exceed 50C. Isn't 50C is the limit for ENT?
Funny how the CMP's make code changes all the time without data or a history of problems, but when we try to get a code deleted or changed they say "oh there's no data to support that change". The whole organization and process is very incompetent and dysfunctional.Not really as I don't have any data for a technical substantiation to support such a change. without such data the it is very likely the PI will be resolved (rejected) at the first draft meetings.
I don't get it. In an earlier post you state that you'd prefer steel flex instead of aluminum to protect against nails. Now you're asking about using smurf.Would ENT (smurf tube) be sufficient as a conduit or would a EMT be required. I am thinking that a continuous load of 48A running though wires encased in closed cell foam for 6 hours will likely cause the temperature inside the conduit to exceed 50C. Isn't 50C is the limit for ENT?
I like the Chicago area & suburbs.............everything is in steel conduit. We don't have to do all those calculations and figure out wiring methods [ie: romex, SE, etc] Just run the conduit & install the wire per code [ie: wire fill & derating values]I don't get it. In an earlier post you state that you'd prefer steel flex instead of aluminum to protect against nails. Now you're asking about using smurf.
Personally, I'd use EMT.
I mentioned the reason earlier. The electrician said it was too difficult to install EMT since it would involve two to three 90 degree turns and passing between holes in studs. I want the wire and conduit hidden inside the wall before foam insulating and sheet rocking. Is it really that difficult or is he exaggerating?I don't get it. In an earlier post you state that you'd prefer steel flex instead of aluminum to protect against nails. Now you're asking about using smurf.
Personally, I'd use EMT.
Without seeing the actual existing construction, it's impossible to make an accurate determination on installation difficulty. But considering this is an unfinished garage, it should not be too difficult to install EMT. There is nothing that requires a bend to be made in the middle of a 10 foot stick of conduit. In other words, a 90 degrees bend can be joined to straight runs with connectors.I mentioned the reason earlier. The electrician said it was too difficult to install ENT since it would involve two to three 90 degree turns and passing between holes in studs. I want the wire and conduit hidden inside the wall before foam insulating and sheet rocking. Is it really that difficult or is he exaggerating?
For this reason I am considering alternatives such as flexible conduit, FMC, or even no conduit NM 3 conductor 4 awg like this
Without seeing the actual existing construction, it's impossible to make an accurate determination on installation difficulty. But considering this is an unfinished garage, it should not be too difficult to install EMT.