Tesla EV charger/eaton breakers

Exception#2 is unenforceable. What is the definition of "unwanted tripping". What does it mean to inform the manufacturer? Do you need to give the manufacturer time to correct the issues. or can you replace the breaker immediately after notification?
Many states have similar exemptions where GFCI' or AFCI's can be omitted, I bet @wwhitney could write it up professionally and summit a PI, indeed that was no final draft just getting the idea out there.
Someone on here was posting about MA has a standard form for unwanted tripping an electrician can fill out ?

The current exception in Oregon reads as follows:
210.12 Exception No. 3: AFCI protection shall not be required for optional, dedicated outlets that supply equipment
known to cause unwanted tripping of AFCI devices.


I never had to use the exception but its there and I am sure EC's use it, all thats required is the EC to state its 'known to cause unwanted tripping' So I doubt they would want more than that from a similar proposal. We'll see.
 