looked through some previous threads but, here I am.
We're planning on using a tesla charger to provide battery backup a traffic signal (load is ~3 amps) during the Public Safety Power Shutoff (PSPS) in California . Tesla has not been helpful. They won't provide much technical information unless where at the point of ordering the unit. the idea is to run the signal on utility power and when there's an outage switch to the charger as a power source. the input to the charger will be utility or solar power.
I found the installation manual online but still have some things to confirm or deny:
Assuming this will work, the maximum charging current in the specs, will be 80 A (thinking this is on 120 V, with the actual current being dependent on the charger.)
On one web page (not the manual) it says peak power is 7 kW, which, at 120 V and a continuous load is around 79 Amps - so, an 80 A breaker. At 240 V, it's half of that so a 40 A breaker.
It says to use a 100 A breaker for fastest charging. However, don't think I can go lower anyway, because it's in the manufacturer's instructions.
Your time and comments are much appreciated.
We're planning on using a tesla charger to provide battery backup a traffic signal (load is ~3 amps) during the Public Safety Power Shutoff (PSPS) in California . Tesla has not been helpful. They won't provide much technical information unless where at the point of ordering the unit. the idea is to run the signal on utility power and when there's an outage switch to the charger as a power source. the input to the charger will be utility or solar power.
I found the installation manual online but still have some things to confirm or deny:
Assuming this will work, the maximum charging current in the specs, will be 80 A (thinking this is on 120 V, with the actual current being dependent on the charger.)
On one web page (not the manual) it says peak power is 7 kW, which, at 120 V and a continuous load is around 79 Amps - so, an 80 A breaker. At 240 V, it's half of that so a 40 A breaker.
It says to use a 100 A breaker for fastest charging. However, don't think I can go lower anyway, because it's in the manufacturer's instructions.
Your time and comments are much appreciated.