I need advice for sizing some transformers. I have a test kitchen that has two cooking sections in the same room. One section will have (4) 208v / 3Ph 17KW electric fryers. The second section has (3) of the same fryers and (2) 208 / 1 Ph / 2700 watt griddles. In addition to this is a walk-in freezer and cooler. I do not have exact specifications, just told 20 amp / 208 / 1Ph circuit needed for each.
This is the set up: Each "section" as I call it is actually a portable wall with a vent hood, suppression system, and the electrical outlets for the above listed appliances already installed. On the other side of this wall is a 225 amp MLO / 3 Ph Square D QO panel. All I am required to do is feed the panels, plus the branch circuits for the cooler & freezer.
The MDP is 480V. I am planning to install a 75 KVA transformer for the wall that only has the (3) big fryer loads and fusing it at 200 amps. I will feed the freezer & cooler from this same panel (I will be installing a 200 amp MB panel with feed thru lugs going to the wall panel and using the busbar to catch freezer / cooler circuits)
For the second wall, I am planning to install a 112.5 KVA transformer and fusing that panel at 225 amps. Is this overkill? I know in sizing commercial kitchens that I can calculate (4) appliances at an 80% demand factor based upon Table 220.56. However, I know when they start up initially all will be heating simultaneously. I also assume they may cycle at the same rate, or close to it. This is the reason for jumping to the larger transformer.
Thoughts / recommendations?
Thank you for your help
This is the set up: Each "section" as I call it is actually a portable wall with a vent hood, suppression system, and the electrical outlets for the above listed appliances already installed. On the other side of this wall is a 225 amp MLO / 3 Ph Square D QO panel. All I am required to do is feed the panels, plus the branch circuits for the cooler & freezer.
The MDP is 480V. I am planning to install a 75 KVA transformer for the wall that only has the (3) big fryer loads and fusing it at 200 amps. I will feed the freezer & cooler from this same panel (I will be installing a 200 amp MB panel with feed thru lugs going to the wall panel and using the busbar to catch freezer / cooler circuits)
For the second wall, I am planning to install a 112.5 KVA transformer and fusing that panel at 225 amps. Is this overkill? I know in sizing commercial kitchens that I can calculate (4) appliances at an 80% demand factor based upon Table 220.56. However, I know when they start up initially all will be heating simultaneously. I also assume they may cycle at the same rate, or close to it. This is the reason for jumping to the larger transformer.