N nickelec Senior Member Location US Jan 3, 2018 #1 Having issues with this question Calculate the short ckt current of a 100kva transformer 120/208 with an impedance of 7% Sent from my SM-G950U using Tapatalk
Having issues with this question Calculate the short ckt current of a 100kva transformer 120/208 with an impedance of 7% Sent from my SM-G950U using Tapatalk
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jan 3, 2018 #2 I am no expert but I believe you need a whole lot more info such as wire size , distance, conduit type, al vs cu, etc
I am no expert but I believe you need a whole lot more info such as wire size , distance, conduit type, al vs cu, etc
david luchini Moderator Staff member Location Connecticut Occupation Engineer Jan 3, 2018 #3 100000/208/1.732/0.07=3954A
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jan 3, 2018 #4 Here is link showing how to do it. http://www.cooperindustries.com/con...rary/BUS_Ele_Tech_Lib_Electrical_Formulas.pdf
Here is link showing how to do it. http://www.cooperindustries.com/con...rary/BUS_Ele_Tech_Lib_Electrical_Formulas.pdf
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jan 3, 2018 #5 david luchini said: 100000/208/1.732/0.07=3954A Click to expand... Dopey me - I was thinking of the aic from the trany...duh...