Hello all,
I am new to the Mike Holt Forums. I am a 2nd year apprentice with IBEW local 20 in DFW. I am studying for a test i have soon and i am confused on how to use this table.
My study question is:
What is the maximum current allowed on a #10 THE when in a conduit with five other current carrying #10 THW's and two bare #10 grounding conductors? (all are copper conductors)(this is a total of 8 conductors in the conduit).
The correct answer is 28 amps. But i am confused on how to arrive at this answer. I understand that the table adjusts 70% for 7-9 conductors. But if table 310.15 b 16 gives a 35 amp ampactiy for #10 THW, why do i arrive at 24.5 amps for the adjustment?
My calculation is
70% of 35 amps. 35*.7= 24.5
I don't get it. Please help!!!!