(E) Busbars.
(1) General. Busbars shall be sized based on 1000 amperes per square inch for copper and 750 amperes
per square inch for aluminum.
Exception: In service switchboards, generator paralleling switchboards and when connecting to devices
rated over 2500 amperes. See 408.60(E)(2) and (E)(3) below.
(2) In Service Equipment And Switchboards Supplied Directly From Separately Derived Systems.
Line-side busbars in service switchboards and all busbars in generator paralleling switchboards shall be
considered service conductors and shall comply with the requirements of 230.42(A).
(3) Connection to Devices Rated over 2500 Amperes. Busbars shall be sized in accordance with (a)
and (b) below when connected to a device (switch or circuit breaker) over 2500 amperes:
(a) Over 2500 amperes but less than 5000 amperes, busbars shall be sized based on 800 amperes
per square inch for copper and 600 amperes per square inch for aluminum.
(b) 5000 amperes and over, busbars shall be sized based on 700 amperes per square inch for
copper and 525 amperes per square inch for aluminum.
Exception: Beyond a minimum distance of 1.2m (4 ft) along the current path from the device, the busbar
may be reduced in size, in accordance with 408.60(E)(1) above.