I have a test prep question for exam. I was looking for a little insight why its not 3/0 in 75 colum. I did choose 3/0 but answer key shows 2/0. 2/0 is good for 150 in 90 degree column


Question. After all demand factors have been taken into consideration for a one family unit a demand load of 35,976VA is determined. What Minimum size thwn aluminum ungrounded service entrance conductors are required for the house with 120240 1ph system?

A 1 AWG
B 1/0 AWG
C 2/0 AWG
D 3/0 AWG
 
What Jumper said. :)

35976/240=149.9 amps
149.9*83%=119.9 amps

Minimum conductor size is 119.9 amps.
 
where did the 83% come from?

The question is at the end of the Unit I am studying where all the other demand factors have been determined. The 35,967 VA is the last question to determine the size Aluminum ungrounded service conductors. Basically the answer is determined by I=P/E and find the wire in T 310.15. I appreicate the answers
 
where did the 83% come from?

The question is at the end of the Unit I am studying where all the other demand factors have been determined. The 35,967 VA is the last question to determine the size Aluminum ungrounded service conductors. Basically the answer is determined by I=P/E and find the wire in T 310.15. I appreicate the answers

For resi services and main power feeders see 310.15(B)(7), there is where you get the 83%.
 
For resi services and main power feeders see 310.15(B)(7), there is where you get the 83%.


The study guide I have was given to me by a co worker. The prep test is 2008. There was a table 310 15 B 6. I am just looking over prep questions and I knew that would be problem with old study guide.Thanks I really do appreciate
 
310.15(B)(7)


(7) Single-Phase Dwelling Services and Feeders. For onefamily
dwellings and the individual dwelling units of two-family
and multifamily dwellings, service and feeder conductors
supplied by a single-phase, 120/240-volt system shall be permitted
to be sized in accordance with 310.15(B)(7)(1) through
(4).
For one-family dwellings and the individual dwelling units of
two-family and multifamily dwellings, single-phase feeder
conductors consisting of 2 ungrounded conductors and the
neutral conductor from a 208Y/120 volt system shall be permitted
to be sized in accordance with 310.15(B)(7)(1) through
(3).
(1) For a service rated 100 through 400 amperes, the service
conductors supplying the entire load associated with a
one-family
dwelling, or the service conductors supplying
the entire load associated with an individual dwelling unit
in a two-family or multifamily dwelling, shall be permitted
to have an ampacity not less than 83 percent of the service
rating.
(2) For a feeder rated 100 through 400 amperes, the feeder
conductors supplying the entire load associated with a
one-family
dwelling, or the feeder conductors supplying
the entire load associated with an individual dwelling unit
in a two-family or multifamily dwelling, shall be permitted
to have an ampacity not less than 83 percent of the feeder
rating.

(3) In no case shall a feeder for an individual dwelling unit
be required to have an ampacity greater than that specified
in 310.15(B)(7)(1) or (2).
(4) Grounded conductors shall be permitted to be sized
smaller than the ungrounded conductors, if the requirements
of 220.61 and 230.42 for service conductors or the
requirements of 215.2 and 220.61 for feeder conductors
are met.
Where correction or adjustment factors are required by
310.15(B)(2) or (3), they shall be permitted to be applied to
the ampacity associated with the temperature rating of the
conductor.
 
The study guide I have was given to me by a co worker. The prep test is 2008. There was a table 310 15 B 6. I am just looking over prep questions and I knew that would be problem with old study guide.Thanks I really do appreciate

It used to be a chart. Same answer, for 150A resi service, 2/0 AL