electricmanscott
Senior Member
- Location
- Boston, MA
- Occupation
- Massachusetts Master Electrician, one man show.
I just failed a final inspection an a new house. The reason cited was one of the AFCI breakers would not trip. I went out to the house and hit the test button and of course it tripped. I called the inspector to find out what the deal was. His tester would not trip the afci. Thanks to this site I know that the button is the only UL approved way to test the breaker but I called SQ D to double check. I relayed this info to the insp but he insists his tester is the right way and if it works on one breaker it has to work on all otherwise the breaker is bad. I got his tester info and called Ideal. They acknowledge what I tell them and confirm the tester is not compatible with SQ D breakers. There is a chip upgrade for the tester but even with that the button is the "Official" way to test the breaker. Called back inspector let him know all this info and STILL he would not sign off as he felt he was putting the town on the line. Told him AGAIN manuf of breaker and tester agree breaker button test is fine and valid and he has no choice but to sign off. Reluctantly he agrees. Here is the kicker, he tells me all the other guys usually change out the breakers till they work with his tester. I told him there is no chance of me doing this as I already now have two hours into this non issue that I can't really bill to anyone. Moral of story, don't beleive everything an inspector tells you.